Carnot heat pump is not realistic #3355
Replies: 1 comment 4 replies
-
The model
The COP is probably that high as it computed based on the fluid temperatures, which at initialization may be close together. See https://simulationresearch.lbl.gov/modelica/releases/v9.1.0/help/Buildings_Fluid_HeatPumps.html#Buildings.Fluid.HeatPumps.Carnot_TCon for the equation that is used. After startup you should get reasonable values. For the |
Beta Was this translation helpful? Give feedback.
-
I have been surfing through the water-to-water heat pumps in Buildings library, and I found there is an important remark to make about the model
Buildings.Fluid.HeatPumps.Carnot_TCon
. I do not understand why the outlet heat flow at the condenser grows with the condenser temperature. Ideally, a heat pump should show a decreasing heat capacity as the required Temperature at the condenser is rised.Apart from it, COP value shows unrealistic values when the heat pump is considered in OFF mode. I wish I knew more about Modelica to dig into the code of the inherited classes and solve it...
I see that alternative models like the
Buildings.Fluid.HeatPumps.ReciprocatingWaterToWater
performs in a more realistic way, although its defining parameters are not really useful. It is difficult to translate "Piston Displacement", "Superheating at evaporator", "Heat transfer coefficients at evaporator and condenser" (among others) into "nominal heat capacity" or "nominal mass flows". Any ideas to overcome this...?Thank you
Beta Was this translation helpful? Give feedback.